Boilers ..... Again
#1
Posted 01 October 2013 - 06:09 PM
When cold the water pressure drops, to the point where the boiler warns of low water pressure and sometimes won't fire up.
Here is a pic of the warning low pressure this evening, the boiler did fire up.
Put a bit more water in I hear you say, well once up to temperature the pressure is bordering on the red, see this picture 30 mins later, i hadn't put any more water in just to be clear.
Poor quality but you get the idea.
In fact this morning I had to take some water out of the system as the boiler kept shutting off as the pressure went too high.
I hate this balancing act and on the odd occasion returning home to a cold house because of low pressure.
Thoughts welcome although I'm not sure what options their are considering the boiler is new.
#2
Posted 01 October 2013 - 06:15 PM
#3
Posted 01 October 2013 - 06:16 PM
expansion vessel is either fcuked or just needs pumping up with a foot pump
get the water pressure down to 0 then connect a foot pump to the schreider valve on the vessell (big fcuk off red thing usually on the back of the boiler) pump it to 1 bar or 14 psi depending how old you are ?
the vessel has a diaphragm seperating the air from the water and as the water is heated it needs to expand somewhere so compresses the diaphragm/air pocket
hope this makes sense
if it is still no good and the pressure in the vessel disapears its fcuked i am afraid and needs a new one
let me know how you get on
#4
Posted 01 October 2013 - 06:18 PM
#5
Posted 01 October 2013 - 06:19 PM
Ironic as on thursday my boiler is being taken out as the expansion vessel has gone. Fluctuating pressure was my symptom. Pain in the arse and costly.
dont get stiffed
if the existing vessel is not leaking you can fit a remote one on the pipework anywhere
they are about 40 quid to buy and take about half hour to fit
as long as it is the same volume as the manufacturers one it will work fine no need to remove boiler and fit oem parts in this case
#6
Posted 01 October 2013 - 06:20 PM
#7
Posted 01 October 2013 - 06:25 PM
Well what do I know I guess. He checked the vessel in front of me and it was pissing water. The boiler makes an odd hissing noise when it turns on.
guess it is leaking then but can be replaced you dont need a new boiler but depends on age and general condition
hissing is probably just surface boiling of the water
I WASNT TAKING THE p*ss just a comment that its the time of year when un suspecting houseowners are ripe for ripping off by some in the trade
#8
Posted 01 October 2013 - 06:30 PM
#9
Posted 01 October 2013 - 06:57 PM
Chris your help is invaluable!!! New expansion vessel was not that expensive just the work of removing boiler to get at it thats the ball ache. He is also fitting a new shower as well when he is here.guess it is leaking then but can be replaced you dont need a new boiler but depends on age and general condition hissing is probably just surface boiling of the water I WASNT TAKING THE p*ss just a comment that its the time of year when un suspecting houseowners are ripe for ripping off by some in the tradeWell what do I know I guess. He checked the vessel in front of me and it was pissing water. The boiler makes an odd hissing noise when it turns on.
#10
Posted 01 October 2013 - 06:59 PM
No problem mate just don't like the thought of anyone getting stitched upChris your help is invaluable!!! New expansion vessel was not that expensive just the work of removing boiler to get at it thats the ball ache. He is also fitting a new shower as well when he is here.guess it is leaking then but can be replaced you dont need a new boiler but depends on age and general condition hissing is probably just surface boiling of the water I WASNT TAKING THE p*ss just a comment that its the time of year when un suspecting houseowners are ripe for ripping off by some in the tradeWell what do I know I guess. He checked the vessel in front of me and it was pissing water. The boiler makes an odd hissing noise when it turns on.
#11
Posted 01 October 2013 - 07:02 PM
If you look behind the boiler and the vessel is there it will be a flat ( about 4 inches ) deed and 18 inches diameter the valve should be on the top but as with all manufacturers of anything it could be on the bottom or side but is just like a tyre valve The other position is behind the control panel and you can't miss it if its there 😃Cheers Chris, sounds straight forward and sensible. I've never fcuked about with a boiler before. Expect a picture of a boiler in a couple of days with the panel removed and me asking where the schreider valve is.
Edited by christhegasman, 01 October 2013 - 07:03 PM.
#12
Posted 01 October 2013 - 07:12 PM
Its a Worscester Bosch combi serving three floors with low London water pressure. Not ideal. Whats your thoughts on Salamander pumps?No problem mate just don't like the thought of anyone getting stitched upChris your help is invaluable!!! New expansion vessel was not that expensive just the work of removing boiler to get at it thats the ball ache. He is also fitting a new shower as well when he is here.guess it is leaking then but can be replaced you dont need a new boiler but depends on age and general condition hissing is probably just surface boiling of the water I WASNT TAKING THE p*ss just a comment that its the time of year when un suspecting houseowners are ripe for ripping off by some in the tradeWell what do I know I guess. He checked the vessel in front of me and it was pissing water. The boiler makes an odd hissing noise when it turns on.
#13
Posted 01 October 2013 - 07:25 PM
So
Drain water to 0 psi, pump vessel up to 14psi, fill water back up to normal level, bleed radiators. Done?
#14
Posted 01 October 2013 - 07:30 PM
Never had to fit one and they ain't cheap The theory seems sound that if you install a pressure booster it will correctly increase the pressure of the water you get through the Taos but if the delivery of water is poor so low flow it will be difficult to improve Is the flow upstairs bad compared to downstairs You really need about 20/25 litres a minute out the downstairs cold tap to start with if that's ok but upstairs is a lot less a booster may help but if your downstairs is poor then it will be a bit of a long shot depends if you got the cash to spend They look to sell at about 360 to 400 quid plus about 50 to install I guessIts a Worscester Bosch combi serving three floors with low London water pressure. Not ideal. Whats your thoughts on Salamander pumps?No problem mate just don't like the thought of anyone getting stitched upChris your help is invaluable!!! New expansion vessel was not that expensive just the work of removing boiler to get at it thats the ball ache. He is also fitting a new shower as well when he is here.guess it is leaking then but can be replaced you dont need a new boiler but depends on age and general condition hissing is probably just surface boiling of the water I WASNT TAKING THE p*ss just a comment that its the time of year when un suspecting houseowners are ripe for ripping off by some in the tradeWell what do I know I guess. He checked the vessel in front of me and it was pissing water. The boiler makes an odd hissing noise when it turns on.
#15
Posted 01 October 2013 - 07:40 PM
#16
Posted 04 October 2013 - 07:02 PM
#17
Posted 04 October 2013 - 07:12 PM
New boiler ? Would be a condensing unit supposed to be more efficient and scrub heat out if the exhaust gasses by product of this is condensation Shouldn't be running much ? Usually drips or dumps via a syphon about half a pint at a time Hope he has made sure it is insulated and not vulnerable to freezing in bad weather or the boiler will fail safe Personally don't like putting it over a gutter, what it it dripping into ? prefer to go straight into a down pipe or sink waste etcHad all work done today and new shower fitted. Boiler is running so much better. Question - there is a white pipe which exits just under my guttering which now has water running out of it. I am assuming that this is an overflow for the tank? Odd thing is I am sure I don't use my tank any more and don't see how this is related to the work done today?
Edited by christhegasman, 04 October 2013 - 07:13 PM.
#18
Posted 04 October 2013 - 07:15 PM
Edited by Goosenka, 04 October 2013 - 07:16 PM.
#19
Posted 04 October 2013 - 07:24 PM
Edited by christhegasman, 04 October 2013 - 07:25 PM.
#20
Posted 04 October 2013 - 07:27 PM
sorry mate missed this post but yep that's the idea assuming when you have drained the water a tyre pressure gauge on that valve will show a lot lower than 14 psiHere
So
Drain water to 0 psi, pump vessel up to 14psi, fill water back up to normal level, bleed radiators. Done?
Edited by christhegasman, 04 October 2013 - 07:27 PM.